Diesel Generator low frequency on high load.

A place to exchanges questions and ideas of a technical / procedural nature. Go ahead, try to stomp us !
sabih
Bilge Dweller
Posts: 2
Joined: Wed Apr 13, 2016 5:56 am
Currently located: Pakistan Karachi

Diesel Generator low frequency on high load.

Postby sabih » Thu Jun 16, 2016 11:23 pm

Dear sir,
I have diesel generator of 630KW capacity installed onboard. We have recently conducted its 3000hrs routine in which we have carried out following work:
1- Removal and cleaning of all heads.
2- All cylinders and pistons were de-carbonized.
3- Gauging of valve guides.
4- Valve grinding and lapping.
5- Injector testing.
6- Testing of cylinder heads.
7- Overhauling of fuel pumps.
It is pertinent to mention that we did not touch its governor. and alternator side. But upon trial, we are facing a problem that after 350KW load, its frequency starts decreasing. We have then also cleaned its turbocharger and its accessories but the problem persists.

Plz help me with your knowledge that what could be the reason of frequency decrease.

User avatar
JK
Enduring Contributor
Posts: 2676
Joined: Tue Sep 04, 2007 2:29 am
Currently located: East Coast, Canada

Re: Diesel Generator low frequency on high load.

Postby JK » Fri Jun 17, 2016 6:05 am

Have you done any compression readings on the engine. If it worked before the overall, there is something up with the engine. Obviously.
Did you use OEM parts? Bootlegged injectors are the kiss of death

Revolver
Day Working Engineer
Posts: 181
Joined: Tue Jun 07, 2011 7:55 pm

Re: Diesel Generator low frequency on high load.

Postby Revolver » Fri Jun 17, 2016 5:52 pm

Steadily decreasing to the under frequency trip, and manually bringing freq up before the trip has it continue to drop steadily, yeah. And gov wasn't touched...
Hrmm.

Like jk said, oem parts? And injector tests were spot on...

All potential air was properly bled from fuel pump over haul?
No stickey parts in the fuel pumps, keep a good eye on the fuel rack. A mix of oil + diesel is usually good to get them loosey goosey, make sure there's no sticking going on.

User avatar
The Dieselduck
Administrator
Posts: 2683
Joined: Sun Jul 22, 2007 1:41 pm
Currently located: Nanaimo, British Columbia, Canada (West Coast of Canada)

Re: Diesel Generator low frequency on high load.

Postby The Dieselduck » Sat Jun 18, 2016 6:19 am

Do you have enough fuel to the machine? check the stack, if not blowing a bit of black under that kind of load, maybe she's starving for fuel. I would check the simple things should be checked first - filters, fuel valves position, fuel pressure, etc.
Martin Leduc
Certified Marine Engineer and Webmaster
Martin's Marine Engineering Page
http://www.dieselduck.net

User avatar
Merlyn
Fleet Engineer
Posts: 747
Joined: Wed Dec 25, 2013 7:19 am
Currently located: South Coast UK

Re: Diesel Generator low frequency on high load.

Postby Merlyn » Sat Jun 18, 2016 11:53 am

Dragging in air thro' a union let go for stripping?
Is it CR or older straight mechanical job?
Remembering The Good Old days, when Chiefs stood watches and all Torque settings were F.T.

sabih
Bilge Dweller
Posts: 2
Joined: Wed Apr 13, 2016 5:56 am
Currently located: Pakistan Karachi

Re: Diesel Generator low frequency on high load.

Postby sabih » Mon Jun 20, 2016 10:43 pm

JK wrote:Have you done any compression readings on the engine. If it worked before the overall, there is something up with the engine. Obviously.
Did you use OEM parts? Bootlegged injectors are the kiss of death


All parts are original as per OEM and technical manual but the the problem persists.

User avatar
Merlyn
Fleet Engineer
Posts: 747
Joined: Wed Dec 25, 2013 7:19 am
Currently located: South Coast UK

Re: Diesel Generator low frequency on high load.

Postby Merlyn » Fri Jun 24, 2016 3:59 am

How goes the genset RPM?
Remembering The Good Old days, when Chiefs stood watches and all Torque settings were F.T.

User avatar
D Winsor
Superintendent
Posts: 325
Joined: Thu Nov 22, 2007 8:23 am
Currently located: Dartmouth

Re: Diesel Generator low frequency on high load.

Postby D Winsor » Fri Jun 24, 2016 5:32 am

I understand the governor wasn't touched but was the linkage to the fuel rack disconnected from the governor?
If so you should check to make sure it was placed back in the correct position on the governor spline shaft or linkage connection points. If the linkage is in the wrong position or the wrong length the governor and or fuel rack will reach it's maximum travel or load limit setting before maximum load is reached on the engine causing the engine to slow down at high loads. I've seen this many times on overhauled engines with mechanical actuators and governors such as the Woodward UG8 or similar type Governors
Troubleshooting 101 "Don't over think it - K.I.S.S. it"

User avatar
Merlyn
Fleet Engineer
Posts: 747
Joined: Wed Dec 25, 2013 7:19 am
Currently located: South Coast UK

Re: Diesel Generator low frequency on high load.

Postby Merlyn » Fri Jun 24, 2016 7:52 am

Wonder how the new fangled Rolls Royce Remote control boys would handle this from their control room thousands of miles away?
You know, the people that are going to make us all redundant ?
It's bad enough trying to sort a remote problem out without even being on the scene.
How are they going to whip the linkages off and physically bar it up against the stop remotely?
How are they going to adjust the max rpm stop?
But is it common rail or straight mechanical?
What engine can it be and what model?
Remembering The Good Old days, when Chiefs stood watches and all Torque settings were F.T.

User avatar
Merlyn
Fleet Engineer
Posts: 747
Joined: Wed Dec 25, 2013 7:19 am
Currently located: South Coast UK

Re: Diesel Generator low frequency on high load.

Postby Merlyn » Thu Jun 30, 2016 6:06 am

Genset seized up then?
Or is it a " so that's all it was then jobby ? "
Shhhhhhhh.
Must have been trapped air on that bend I told you about said the voice.
H.E. Jobby?
Remembering The Good Old days, when Chiefs stood watches and all Torque settings were F.T.

User avatar
Merlyn
Fleet Engineer
Posts: 747
Joined: Wed Dec 25, 2013 7:19 am
Currently located: South Coast UK

Re: Diesel Generator low frequency on high load.

Postby Merlyn » Tue Jul 19, 2016 9:49 am

Ah well, looks like the genset has gone the same way as pushrods Pete ( Frank Perkins article re the bent pushrods since turbo change? )
Now we will never know the outcome.
I reckon a Shhhhh jobby.
Don't say anything but ...........
Remembering The Good Old days, when Chiefs stood watches and all Torque settings were F.T.